IOT Gateway Doesn't see all RAPID variables
Options
XNOR
✭
Recently connected IOT Gateway to a IRC5 running RobotWare 6.05.02. I then have an ignition gateway connected to the IOT Gateway for an HMI. I can see any variables that are defined PERS but not VAR or CONST.
I would expect VAR or CONST to at least be available as read-only. Is this typical with all versions of RobotWare?
I would expect VAR or CONST to at least be available as read-only. Is this typical with all versions of RobotWare?
Tagged:
0
Best Answer
-
Hello XNOR,
Please refer to the IoT Gateway manual https://robotapps.blob.core.windows.net/apps/ApplicationManual IoT Gateway v1.1.pdf
More specifically section called "Subscription for data changes" on page 47.
I.e. only persistent variables are available from the RAPID domain.
—Maxim RiabichevPC Software Support Engineer1