PC Interface function at the IRC5

Hi

I'm going to connect to Webware server, So included PC interface option to the IRC5 controller. But I can't find Application Portocols manu on TPU monitor.

Please let me know how can I LAN setting. Please refer to the attached files.



Robot Model: IRB340 PickMaster

Controller: IRC5

RW Ver.: 5.06.0.0143



2006-03-29_110900_S3700003.zipshcho2006-3-29 11:12:44

Comments

  • There aren't any settings to configure for PC Interface, you just need to set your IP address.

    To set the IP address, you must X-Start your  controller into the boot loader application and use the Settings menu to either set it up to use DHCP or to specify a static IP address.

    Russell Drown
  • Just a small clarification for other readers.

    To connect to WebWare Server/SDK you need to have a robotware option.
    On S4C+ this is FactoryWare Interface.
    On IRC5 this is PC Interface.

    S4C+ with FactoryWare Interface has Application Protocols that need to be properly set up as per the manual.

    IRC5 with PC Interface is preconfigured and thus requires no action.