Group IO Bit Size

How many bits is the max for group IO?  I assumed 32 bits but I'm only seeing 16.

Comments

  • We use 32bit in our IRC5. We send/receive 256 in/out from the Anybus Ethernet adapter and group them in 32 bit Group variables. 
  • Thanks YoDoug.  I just found my issue to be the UDT on the AB PLC side.
  • lemster68
    lemster68 ✭✭✭
    Interesting note to add.  With newer robotware they no longer have to be contiguous bits, you can split it up.
    Lee Justice