System Failure

SomeTekkSomeTekk USA
edited June 2019 in Robot Controller
Twice now a running RW 5.15 system has entered a system failure state for no detectable reason. 

No hardware issues required correction. No programming or parameter changes occurred prior to the failure. Both times a B-Start was able to get the system operational.

A strange item related to both incidents is a gap in the event log, one time for nearly 3 weeks, the most recent occurrence the gap was approximately 10 days. The system operated without issue during the days there seemed to be no event logging happening.

2711101 E    System               20195 System data from last shutdown is lost   6/15/2019 15:02 Normally, all system data is saved on shutdown. During the last shutdown saving data has failed. The system has been started using last good system data saved earlier at WED JUN 05 07:14:50 2019.  {args: "WED JUN 05 07:14:50 2019", "WED JUN 05 07:14:50 2019"}
2711100 E    System               20205 Auto Stop open                           6/5/2019 7:14 The Automatic Mode Safeguarded Stop circuit has been broken. {args: }

There are more than 20 other systems similar to this system and none of the others, which have the same environmental conditions (mains power is stable), have experienced this production-killing problem.

This is an ABB non-robot manipulator system of the FlexLean track and lifter combo type.

Has this scenario happened to anyone else, and if so was a resolution found?


Post edited by SomeTekk on

Comments

  • lemster68lemster68 United States ✭✭✭
    I haven't heard of that before.  Did you look at all your event logs to see if there is an error causing the sysfail?  Also, did you try B-Start?  I-Start seems harsh, but if you have to, you have to.
    Lee Justice
  • Hello Lemster,

    Yikes, I had to edit the original post. A B-start solved (temporarily{?})both instances.

    All logs were examined and both times no "smoking gun" was found. In the original post the events listed are sequential, the last one on 6/5 (2711100) - the next one was after the B-Start on 6/15 (2711101).

    The first time this happened logs, backups and system diagnostics were sent to the local ABB office and a R## ###k case opened. Unfortunately no luck in finding a root cause was found. 
  • lemster68lemster68 United States ✭✭✭
    Maybe from time to time you can check on the program resources, cpu load memory usage.  One thing I have seen before is execution stack overflow due to a recursive program.  Maybe you can check to see if there is any chance of recursion in your program.
    Lee Justice
  • Sounds good, will do.

    I am familiar how to do that with RS; you don't happen to know if there's RAPID that can accomplish that do you?

  • lemster68lemster68 United States ✭✭✭
    I am not aware of any rapid instructions to read that data.  Just system info button on the pendant, and somewhere in there under the properties.
    Lee Justice
  • SomeTekkSomeTekk USA
    FYI - This was resolved. 

    The 4 pole Phoenix terminal connector that carries power to the Main CPU was barely maintaining contact. As the control sits on a mezzanine in close proximity to a stamping press it is a wonder the problem was as isolated as it was.

    Reseating the connector solved the problem and became a maintenance item for the ABB control population.