CRB15000 OmniCore C30 Controller
jbilby62
Recently, I began having issues powering up my Omnicore C30 Controller. Controller was powering up just fine but then I needed to rerun some wire through wire duct and the power cable was one that needed to be rewired.
Once the power cable was rewired I checked voltage across the load side of my fuse and the neutral terminal block the cable was wired to and I was getting 120 VAC. Just to be sure, I checked the voltage across the pins on the power cable connector and was also getting 120 VAC. I believe the manual said there is no internal fuse and I am fusing the system with a 10A fuse.
The "MS" red light was on for a little bit but then eventually turned off. Is there something internal to the controller that may be blown? No smoke or odors are coming from the controller either.
Thank you
Thank you
Are there any entries in the error logs on startup that may give a clue to where the problem is?0
Currently unable to start up the controller to view any errors.graemepaulin said:Are there any entries in the error logs on startup that may give a clue to where the problem is?0 -
Misunderstood thought it was an intermittent fault...
Please see attached from the product manual.
Page 59/521 gives the LED status and meanings.0
- 350 IRC5
- 848 RAPID Programming
- 21 AppStudio
