IRC 5 Controller Problem
Hello Everyone.
I Have IRB6700 Robot and My Controller is IRC 5.
My Problem;
The robot works but gives warning. What should I do. I measured the voltages, but I did not see any problems. I may still be wrong. What should I consider when measuring. And could something else be the source of the problem?
I Have IRB6700 Robot and My Controller is IRC 5.
My Problem;
" W Hardware 34401 DC link voltage too low warning 2020-06-19 15:00:50 In drive module 1, the drive unit at unit position 1 has a DC link voltage that is close to minimum limit. {args: "1", "1"} "
The robot works but gives warning. What should I do. I measured the voltages, but I did not see any problems. I may still be wrong. What should I consider when measuring. And could something else be the source of the problem?
0
Answers
-
Root cause: The incoming mains voltage to the rectifier unit is out of specification. If the voltage is okay, Check all internal 3-phase components (main switch, mains filter, fuse, contactors) and cabling in the drive module. The last is to replace the Main Drive Unit.
0 -
I replaced the other cables in the pan of the cables where the power cables and other signal cables pass, and the problem solved itself. Why do you think it might have happened? Because I still don't understand.
0
Categories
- All Categories
- 5.5K RobotStudio
- 396 UpFeed
- 18 Tutorials
- 13 RobotApps
- 297 PowerPacs
- 405 RobotStudio S4
- 1.8K Developer Tools
- 250 ScreenMaker
- 2.8K Robot Controller
- 316 IRC5
- 61 OmniCore
- 7 RCS (Realistic Controller Simulation)
- 800 RAPID Programming
- AppStudio
- 3 RobotStudio AR Viewer
- 18 Wizard Easy Programming
- 105 Collaborative Robots
- 5 Job listings