Unable to restore the controller from backup (error code 80001)
Answers
-
Is that a real controller or a virtual controller in RS?Lee Justice0
-
real controller
0 -
In that case I would check to see if the controller has run out of storage space, if possible.Lee Justice0
-
I'm not sure storage space has got much to do with "Stationname must match if interfaces are the same" but there is loads of it
0 -
Yeah, I was overlooking that. What could station name mean? Do you have external axes in this setup?Lee Justice0
-
wish I new, it's just a robot with a built in io module and a profinet connection to a plc. It's a bit of a fundamental flaw if you cant restore the backup that was made the day before!0
-
Search the backup for Stationname.Lee Justice0
-
I have the same problem, when trying to send IO changes to the robot from ioEngineering. i get the error: 80001: Stationname must match if interfaces are the same
I cant find station name anywhere
0 -
so i think the station name gets assigned to the robot by the profinet plc. In the end we gave up trying to used profinet safety signals and hard wired it.0