tcp speed with profibus.
Hi guys.
I have a problem..
? try to transfer tcp speed with dsqc 352 profibus unit (S4C M2000 controller). couldn't find a way to add system output related with tcp speed to the profibus module.
profibus module does not accept AO integration, although system output for tcp speed is AO.
any opinion?

thx
redundant2009-05-15 15:22:29 0
Comments
-
HiYou could put the tcp speed on a sim unit and then read the value of the analog signal in a background task (task1) and set there a group output on the profibus unit. You should ad a wait time in the background task of minimum: WaitTime 0.2;Best regardsMarcel0
-
tnx a lot..