Is it need 616-1 (PC Interface).

Hi
 

     I has 16-63223 that has only flexpendant interface.

     I had load some Screen maker inside this real controller.

      It work!!

 

     I very confuse now , Is it need PC-interface option.?

    

   PC-interface option use for what.

  flexpendant interface option use for what.

 

     Please kindly explain me.

      Thank you so much.

 

Best Regards,

Mr.Robot

Comments

  • Hi... just to build above Sunil commens:
     

    PC Interface - this option allows external clients to connect to the IRC5 Controller. For example, when you are designing your screen inside RobotStudio-ScreenMaker, this option allows the ScreenMaker designer to connect to the IRC5 controller in order to get / set data.

     

    When you are satisfied with the design of your screen, you can build your application and download or copy the DLLs of your screent into the IRC5 controller.

     

    Flex Pendant Interface - this option allows to run customized applications inside the FlexPendant. This option applies only to appliactions which run inside the FlexPendant. In the case of ScreenMaker, you want to run your generated screen inside the FlexPendant. This option allows your ScreenMaker application to run inside the FlexPendant.

     

    BR
    Carlos Martinez
    ABB