IRC5 Ethernet IP Master to C.Logix

Hi,
 

I have an IRC5 with the Ethernet IP Master option. I need an AB Contrologix L61 to be the slave (I eventually will have several L61's as slaves). After missing  a bit of hardware, an incorrect keystring and an out of date baseware version I think I'm pretty close to achieving connectivity. What I am totally confused about is the Assembly Instance at the IRC5 end and the Contrologix end.

 

Anyone ever managed this arrangement?

 

Thank for any info. 

Comments

  • I too am having issues with this same thing.  Does anyone at ABB have some examples of how to get Ethernet/IP communicating with any AB PLC's?

     <?: prefix = o ns = "urn:schemas-microsoft-com:office:office" />

    I'm still trying different configurations such as setting up the robot as an IP_INTERNAL_SLAVE, and trying to make the PLC the master but not sure how to configure the PLC to communicate this way.

     

    Any help or documentation would be greatly appreciated. 

     

    Thanks,

    Toby

  • Hi,
     

    The Rockwell ControlLogix PLC:s don't have the functionallity needed to be able to be connected as a server (internal slave) from another client (master).

     

    To be able to contact the EtherNet/IP internal slave in the IRC5 controller from a PLC it must be configured as a EN_INTERNAL_SLAVE and for example 8 byte in and 8 byte out.

     

    In module proporties for the IRC5 internal slave in RSLogix specify the correct IP address, assembly instances (input: 100 with size: 4 and output: 112 with size 4 and Configuration: 1 with size 0).

     

    Use the Comm Format (communication format): Data - INT

     

    Download and go online and the PLC should have established a connection to the IRC5 internal slave.
  • Thank You for the Info (Worked Great)

    Just wondering how did you figure out the settings
    Tim Ellebracht
    Info Logics Inc.
  • All these parameters can be found in the EDS file.