Has anyone done this before?  I need a silver platter solution.
 

Devicenet seems to be operational, both LED are solid Green.  No activity at all from NAS and 1747-SN is blinking red.

 

Currently I'm integrating this system, this is my first IRC5 controller (brand new) but I've taken IRC5 Programming 1 class and I'm generally familiar with navigation.  I have successfully set up my 652 I/O card.  I've rarely done anything RIO except on FANUC robots years ago.  I'm trying to set up full rack and 128in/ 128 out.  If someone has already set this up before, at any setting, please let me see your files.  I learn by copying others and growing from there.  Right now I got nothing to plant my roots in.

 

EIO FILE


 

RSS FILE


 

Thanks!
spaceacealpha2012-11-26 18:58:46

Comments

  • webwiz/6945/SETUP.zip


    Resolved!
    This is the two files for 128 bit communication back and forth between a IRC5 Controller DSQC-350B series and a 1747-SN B series Remote I/O Gateway.  Example of RIO input and output and Group Input and Output is given.  Pay attention to N7:50 - N7:55, these are the setup files needed to tell the 1747-SN what its talking to.

     

    1747-SN B set up 57k speed with 150 ohm resistor.  I set up DSQC-350B with 150ohm resistor. 

     

    I followed/copied over to ladder pages 144 to 149 in the Manual 1747-UM013-EN-P for a Bi-Directional Continuous update.  Again the only ones I set up is N7:50 to N7:55.

     

    N7:50/7 = on

    N7:51/0 = on (addressing 0)

    N7:52/0 /1 /2 /3 = on full rack

    N7:53 = all off


    N7:54/0 = on (addressing 0)

    N7:55/0 /1 /2 /3 = on full rack

     

    Once this was complete and did a first scan on my PLC, the Scanner COMM light went solid green.

     

    In the Input/ Output listing in the RS Logix I could see my scanner cards 32 available words and could turn on and off bits on either side and see the result on the other side.  This is after setting up SIGNALS in the IRC5, the ones used in the example.

     

    I used 3HAC020676 page 100 for setup on the ABB IRC5 side.

     