Forum Migration Notice
Update (2026-01-21): The user forums are now in read-only mode pending the data migration.
Update (2026-01-12): The user forums will be put into read-only mode on the 21st of January, 00:00 CET, to prepare for the data migration.
We're transitioning to a more modern community platform by beginning of next year. Learn about the upcoming changes and what to expect.
Update (2026-01-12): The user forums will be put into read-only mode on the 21st of January, 00:00 CET, to prepare for the data migration.
We're transitioning to a more modern community platform by beginning of next year. Learn about the upcoming changes and what to expect.
Cannot write IRC5 controller
I install ABB IRC5 OPC Server on a Windows 2000 pro SP4 machine.
Tags are accessed from an OPC client (Iconics genesis 32) and tags are requested only if the customer open the interface page.
Tags are persistent variables.
System works properly, but every 3-4 days customer can read but not write the tags. Customer can enter the field and write a new data, but after few seconds it has the previous value (obviously read from the robot). Our conclusions: new data does not reach the robot and on the the next read request we have the old data.
Please not that the OPC server does not put the tag as readonly when the problem appears.
To solve the problem it is necessary to reboot PC.
Best regards,
Davide
Davide
0
Categories
- All Categories
- 5.7K RobotStudio
- 402 UpFeed
- 21 Tutorials
- 16 RobotApps
- 307 PowerPacs
- 407 RobotStudio S4
- 1.8K Developer Tools
- 251 ScreenMaker
- 2.9K Robot Controller
- 368 IRC5
- 92 OmniCore
- 8 RCS (Realistic Controller Simulation)
- 859 RAPID Programming
- 43 AppStudio
- 4 RobotStudio AR Viewer
- 19 Wizard Easy Programming
- 111 Collaborative Robots
- 5 Job listings