Dsqc 652 and relay
I would like to control an Air valve by setting a digital output signal. For this reason I need to connect a relay to the Dsqc 652 available unit. From the manual it is not clear how to do. Since it seems that the board need to receive 24 V from XT31 connector through a connection between XT31 pin 1 and dsqc 652 x1 pin 10 and  XT31 pin 5 and dsqc 652 x1 pin 9. But after that I don't understand how to connect the relay to the I/O board. I saw that there is a specific I/O board with relay output but I would like to know if what I would like to do is possible also with dsqc 652.
The last question is related to the fact that the I/O unit on flex pendant results "not connected" and no leds are turned on. My controller is IRC5.
Thank you so much for the help.
Perla
  • soup
    soup ✭✭✭
    That card should have no problem triggering a 24v relay. "Not connected" is odd -- no lights and no manually firing an input by connecting it to 24v? If it's not listed in your system by default, I'm sure ABB has a manual for that unit...
  • First you should check the address of your I/O board, usually devicenet address is 10 or 12. Secondly, if you bring in a proper way 24 V DC supply to DSQC 652 you should see LEDs for power status on. Finally you will use output terminal from I/O card and common (your DC supply to card) wire in order to energize relay with I/O board.