Guard Stop State
HChavez
Hi everyone,
Recently I've been working on a IRB4400, irc5 with safe move and multitasking, and yesterday, to be exactly, the robot would go on stop guard state, in Auto and Manual mode.
While I was testing the path in manual mode, the controller would go on stop guard state even though I kept pressing the the enable device. And, during auto mode, it did the same, I started the program and in the middle of the program and almost at the end of the program, the controller entered in guard stop state and I had to press again the ON/OFF motor button to continue the program. And the flexpendant doesn't show any alarm it just goes from motors on to guard state.
I hope you could help me out with this.
Regards.
Regards.
Did you check the error log, as there should be notifications.
This sounds like it could be SafeMove seeing an issue - is it setup and in use?0 -
Graemepaulin,
The event log didn't show anything and I have't configure any SafeMove condition, at all.
Regards0 -
I got it,
the safe move 1 was configured in Synchronization time at 120s, so every 2 minutes the system was on "operation" would ask me for a software sync and the log showed me that I had to do a synchronization. I just adjust the time between each software sync and it hadn't stop.
Regards.0
- 398 UpFeed
- 300 PowerPacs
- 336 IRC5
- 67 OmniCore
- 828 RAPID Programming
- 12 AppStudio