S4C+ Profibus DP slave setup
Hello
What do you do to set up a DSQC 352? I want to control the robot with a PLC (Siemens S7-1200 with Profibus DP master module). What exactly do I need to do? Can't find it on manual or google. I've connected them with the cable.
Thank you
  • Hey!
    I think this is all you have to do in the eio.cfg file.
    You also need to set the device net address correct and also set the correct input/output size in the plc.
    You can read about that in thi link:
    http://host.bglot.com/ABB/ABB_3HAC020676-001_revB_en.pdf
    EIO:CFG_1.0:3:1::
    EIO_UNIT:
          -Name "Profibus" -Type "d352" -Bus "BASE" -Digin 129 -Digout 128\
          -PollRate 100 -Param "Profibus_VAL"
    Profibus_VAL = EIO_PARAM_VALUE:
          -Name "MasterInputSize" -Value "8"
          -Name "MasterOutputSize" -Value "8"
          -Name "StationAddress" -Value "4"
  • Thanks Joar! I got it working. Now I have 128 extra I/O to the PLC:)
  • Hello Jeffdu,
    I have the same configuration:
    - ABB S4C+ controller
    - ABB DSQC352 Profinet
    - Siemens C1214C DC/DC/DC
    - Siemens CM 1243-5 Profibus card
    The ABB is configured as adress 3, and the PLC is configured as adress 2
    But the PLC keeps reporting to have no connection with the ABB controller.
    Could you show how you configured the Siemens PLC for the profibus connection?
    rcool
  • robotmey
    robotmey
    edited February 2022
    hello
    does it require to set DSQC352  same address in both place ?
     In EIO.CFG and jumper pins(X5)?
  • Joar said:
    Hey!
    EIO:CFG_1.0:3:1::
    EIO_UNIT:
    Estou precisando de uma ajuda. Estou querendo comunicar com modulo da Omron (CJ1W-PRM21) Profibus e nao estou conseguindo. usei essa mesma EIO