Issue with Profinet configuration
RegardsCornet RaymondManager+352 621 354 570raymond.cornet@luxrobotic.com
http://www.luxrobotic.comHP ZBook Fury 16 G110 -
There is 2 robots connected to PLC
OK. So, the profinet gateway address from the last configuration is the IP address of this switch?Lee Justice0
Hello,sorry for the late reply.The Ip address of the DSQC-678 board is 192.168.10.51
Hello again. Have you added the EIO_UNIT for the IO, PN_INTERNAL_SLAVE Unit Type? And the switch IP address matches the gateway IP address?Lee Justice0
We are not able to change the current IP address which is 192.168.1.100.As I understood we could only make by generating a xdb file with the PLC software, that we didn't succed until now.
There may be a misunderstanding here. I am not asking you to change the switch IP address, just make the gateway in the EIO.cfg match the switch address.Lee Justice0
If I set the IP address in the cfg file, the PLC doesn’t see the change. This should be linked to the xdb file where the address is still 192.168.1.100.RegardsCornet RaymondManager+352 621 354 570raymond.cornet@luxrobotic.com
Have you created the EIO_UNIT in your EIO?Lee Justice0
The robot is a used one, the config was in the controllerRegardsCornet RaymondManager+352 621 354 570raymond.cornet@luxrobotic.com
Last thing to ask: Have you managed to name the station in profinet using some kind of profinet configuration tool?Lee Justice0
That's the problem we have, we did a lot of tests, without success. Only one time, but just for a few minutes.We can't make any change on IP address or nameRegardsCornet RaymondManager+352 621 354 570raymond.cornet@luxrobotic.com
- 365 IRC5
- 84 OmniCore
